Welding cable Amp and voltage drop

Try to post your problem here, there is a chance, someone clever will help you.

Moderator: convert-me.com

Welding cable Amp and voltage drop

Postby Fitzy » Sun Jul 27, 2008 9:28 am

Gday,
I am trying to work out if 70mmsq/2/0 copper welding cable running up to 150 Amp@30to60 volt is going to be enough over 250m820ft from welding electrode to welder.
I am useing miller 300amp dc welder
Any hepl would be great
Fitzy
 

Re: Welding cable Amp and voltage drop

Postby Guest » Sun Jul 27, 2008 5:10 pm

Fitzy wrote:Gday,
I am trying to work out if 70mmsq/2/0 copper welding cable running up to 150 Amp@30to60 volt is going to be enough over 250m820ft from welding electrode to welder.
I am useing miller 300amp dc welder
Any hepl would be great


Resistivity of copper is about 17 nanohm·meters, but varies a little with temperature. Resistance is
resistivity x length/area

17E-9 ohm·m X 500 m /70E-6 m² = 0.12 ohm
(you have two wires 250 m)

0.12 ohms x 150 A = 18 V

At best, very marginal. Probably the drop is excessive.
Guest
 


Return to Other math problems

Who is online

Users browsing this forum: No registered users and 1 guest

Our Privacy Policy       Cooking Measures Converter       Metric conversions