Voltage Drop

Postby jcash » Mon Apr 12, 2004 8:12 pm

What size aluminum conductor should I use? Service line for a poultry house, 120/240 volt service, 155' from trasformer pole to load site. Estimated load is 190 amps and I can only have a 1.5% voltage drop.
jcash
 
Posts: 1
Joined: Mon Apr 12, 2004 8:00 pm

Re: Voltage Drop

Postby Knight » Tue Apr 13, 2004 2:19 am

jcash wrote:What size aluminum conductor should I use? Service line for a poultry house, 120/240 volt service, 155' from trasformer pole to load site. Estimated load is 190 amps and I can only have a 1.5% voltage drop.
The answer, of course, is that you shouldn't use aluminum at all.

The answer is 350 kCmil wire. tough to find. You'll want to use 4/0 copper in real life.

Check out http://www.electrician.com/vd_calculator.html for a handy voltage drop calculator.

http://www.powerstream.com/Wire_Size.htm has a good reference for finding resistivity of copper wire. all you'll need to remember is that aluminum wire has a k 1.64 times that of copper, and you should be able to convert.
William J. Knight
Health Physicist
Los Alamos National Labs
User avatar
Knight
Expert
 
Posts: 309
Joined: Tue Jan 13, 2004 9:43 pm
Location: Los Alamos, NM

cable size comparison

Postby peter upton » Wed Mar 02, 2005 6:48 am

Knight wrote:
jcash wrote:What size aluminum conductor should I use? Service line for a poultry house, 120/240 volt service, 155' from trasformer pole to load site. Estimated load is 190 amps and I can only have a 1.5% voltage drop.
The answer, of course, is that you shouldn't use aluminum at all.

The answer is 350 kCmil wire. tough to find. You'll want to use 4/0 copper in real life.

Check out http://www.electrician.com/vd_calculator.html for a handy voltage drop calculator.

http://www.powerstream.com/Wire_Size.htm has a good reference for finding resistivity of copper wire. all you'll need to remember is that aluminum wire has a k 1.64 times that of copper, and you should be able to convert.
I am using 4/0 welding cable; what is the equilivent in "HCM" size?
peter upton
 

Re: cable size comparison

Postby Knight » Thu Mar 03, 2005 12:06 am

peter upton wrote:I am using 4/0 welding cable; what is the equilivent in "HCM" size?
I'm not sure what "HCM size" is. AWM 4/0 wire (American Wire Gauge) is 120 mm for metric standard.
William J. Knight
Health Physicist
Los Alamos National Labs
User avatar
Knight
Expert
 
Posts: 309
Joined: Tue Jan 13, 2004 9:43 pm
Location: Los Alamos, NM


Return to Other math problems

Who is online

Users browsing this forum: No registered users and 0 guests

Our Privacy Policy       Cooking Measures Converter       Metric conversions